How to pick a UPS (not PSU) with right capacity?
23 minutes ago, Supersonicwolfe said:So I have a 650 W system (3600+ GTX970, eyeing a RTX3070 and 5600 in future) needs a UPS.
Now, do I need to match the wattage of the UPS with PSU? Or I should be fine as long as the VA capacity is sufficient?
They do not need to be matched. The UPS needs to have a high enough power rating to supply power to the load, just like any power supply, that's all. If the load is 600 W you should get a UPS that has maybe 800 W or more to allow enough headroom.
Apparent power rating (VA) is irrelevant here and should be ignored. It is much higher than the real power rating (W) to allow headroom for devices with low power factor, which put additional load on the UPS without drawing more average power. This is typically motorized devices which have inductive loads with lower power factor. PC power supplies have active power factor correction, so the apparent power is only a little higher than the real power. You just need to look at the Watt rating and make sure your computer and other components don't exceed that. If you had a large inductive motor you might also be worried about exceeding the VA rating, but it really doesn't matter for computers.
What's more important is to get a pure sine wave UPS not a "simulated sine wave" because they can cause issues with active PFC circuits in modern power supplies and may cause your computers to shut down unexpectedly when the UPS is on battery backup power, even if there is plenty of battery left.
QuoteVA calculation (650W computer +50W monitor router)/0.8 = 875 VA
The 0.8 needs to be replaced with the power factor of the load, it's not a constant value. For a PC it's probably closer to 0.95 or 0.9.